Thats interesting! I'd never thought that it would work both ways. I'm intending on trying to get some HID ballasts over. I thought I might check to see if it would work properly. I will still use something along the lines of a converter for if I can't find a 277V ballast. I knew that they sell step-down transformers but I knew that with mainly transformers you can go up in frequency but never down. How would it work if I were using a CWA ballast? Would it work as it should on 240 or undesirable effects with the capacitor?
Same applies to HID chokes and HX, while all the more complicated considerations apply to the other types of ballasts
For chokes, the rule is that you dont want to saturate it. The flux (which if exceeds the designed value, leads to saturation) is related to the current. The current is proportional to voltage and inverse to frequency. So as long as V/F (new) is not higher than V/F (original), you are in the clear
Transformer can be viewed as a combination of 2 devices :
- The "transformer itself" i.e. the voltage conversion according to number of turns. This works always regardless of anything else (as long as it is supplied with AC)
- The magnetization of the core, which acts as a choke. This is, in fact, the choke which consists of the core and the primary winding of the transformer. The magnetization current is the current that goes in the primary winding when there is nothing connected to the secondary (which is, in fact, a choke - consisting of the transformer's primary and the core). This current is largely independent of the load on the secondary. (When the transformer is loaded, the current in the primary is sum of the magnetization current which remains the same + the current which is converted to the secondary)
In the case of choke (designed to act as a choke), the current through it directly affects the current through e.g. lamp, so we just want the current to be the same
In the case of transformer, it is designed to work at a certain magnetization level. If the magnetization will be too high, it will saturate. If lower than designed, it will be able to convert less power, but nothing bad happens
As the magnetization acts as a choke, the current through it is proportional to voltage and inverse to frequency. So, if V/F (new) = V/F (original), the magnetization current will be the same
CWA ballast have 2 components that behave different than a choke :
1. The core of the ballast
A CWA is a magnetic device with some interesting functionality. It is not "just a choke" like a choke or choke-derived ballast designs (HX)
The core of a CWA consists of a thin section of core in the magnetic path of the secondary, which is intended to saturate at a specific flux level. As the magnetic flux is converted back to electrical current on the secondary winding, this behaves as a constant current source (as in constant RMS value, not as in DC)
A gapped shunt between the primary and secondary windings then closes the magnetic circuit for the rest of the flux generated by the primary, which bypasses the secondary
2. The capacitor
As stated before, the capacitor behavior at different frequencies is opposite from a choke