Hello everyone,
I'm posting here because I am having (and want to publicly announce) some unacceptable issues with recent dual-function AFCI and GFCI receptacles. Specifically, I’ve had them either fail prematurely without initial warning, or fail to trip in the presence of a hazardous arc.
Last month, I had a dual-function Eaton receptacle fail without initially giving any warning. Upon doing a monthly test, the red "failed" LED started flashing, meaning the outlet had already been defective for some time prior. While I get that the AFCI portion usually doesn’t “self-test,” unlike the GFCI part, the quality control still seems horrid considering it was less than 3 months old.
Fast forward to now, and I replaced the bad Eaton with a dual-function (GFCI/AFCI) Leviton, which
is stated to have series arc protection. Eventually, curiosity got the better of me, so I decided to put the thing to the test.
Please note I know what I’m doing around electricity, so please don’t attempt what I’m about to describe unless you’re experienced!
Anyways, I started by hooking a stripped power cord to a kalamata olive (no joke), which is similarly conductive to a pickle. It quickly started sizzling and making bright, sputtering yellow arcs before blowing smoke. The AFCI
never tripped during all of this!
Thinking the arcing of the olive may have been too low-current, I then tried something more drastic. I took an extension cord, and cut the neutral conductor. I plugged in a 1500W space heater, and sparked the severed leads. It made bright arcs, turned the insulation black, and made bright orange sputters that even caused the copper to bead! That didn’t work, either. Finally, I took a piece of mechanical pencil lead with a high graphite content, wrapped one end of the severed extension cord wires around it, and then continually arced it with the load connected. Although it sustained a sputtering (and continuous) series arc, the attached load still remained powered on and
the outlet did not detect this. Had this happened in an unknowingly-damaged power cord in the middle of the night, I could have woken up to smoke and flames (if I got lucky enough). Thus, I am seriously questioning if the AFCI is a “gimmick,” especially due to what I’m about to express below.
Investigating further,
it turns out I’m not alone in my issue. An Eaton AFCI breaker, in this video uploaded by a home inspector, failed to trip when an outlet started severely arcing, and almost burned down a house.
See HERE:
https://www.youtube.com/watch?v=pHkJ8maQ-mUSo, in summary, I have reason to doubt that AFCIs really do what they are supposed to, and that they may be giving a false sense of security (at least in terms of series arcs). I’m not sure why it has been so difficult over the years to get them “just right,” and even now, they still seem to be far from perfect. It appears they’re either too sensitive and trip when you try to use a common appliance like a vacuum, or aren’t sensitive enough to detect hazards.
Seems completely unacceptable to me, considering the manufacturers could cost people their lives and/or homes with this type of issue. As the consumer, we entrust that when we receive a product with safety markings (e.g., UL), as well as from what we perceive to be a reputable company, we'd get better than this.