This (the video of the 110kV thing) is not arcing on a switch, but an isolation disconnect. The switch is inside of the horizontal isolator like things, first the switch are suppose to break the load current and then the main arms disconnect all that in a visible manner. The disconnect is designed to operate only with no current, so has no arc quenching, it is tgere just as an extra safety addon. But here one of them failed (there are two in series), the second half gets an overvoltate so keeps arcing over, then the disconnect starts to operate with load (it is not designed for that), so the spectacular arcing (the load here is some phase compensation bank, if I undestood well, so not that huge load).
|
|