I have a question about adding capacitors too. I have a 100w HPS yard light with an OEM 120v S54 reactor ballast. I have a 36uF/120v cap from an Advance 100w HPS 120v S54 reactor ballast kit. Being the same type and wattage of ballast, I would think there would be no problem using the Advance cap on the OEM ballast, but could there be any differences that would mean it would need a different cap? The label on the OEM ballast shows an optional cap but doesn't list values for it.
If the cap is directly connected to the mains, it is only to compensate for the phase shift coming from the ballast (so improve the power factor) of the current drawn from mains, but it has no influence on the ballast functionality, so such capacitor you might connect. It is weird, then the manufacturer does not state the value, as virtually only he know, what inductive current has to be compensated out. But as all series choke should have equivalent behavior, the capacitor for correct compensation would be equal.
But the capacitor charge current causes power surges upon power ON (unless you "hit" the moment, when the voltage is near the zero crossing), so it would cause high current sparks on switch contacts. So i would use the capacitor only on longer wires, where it is really needed (as the uncompensated lamp current would cause too high voltage drop) and where the wire resistance limit the power-up inrush current.