Author Topic: Does low power factor affect electric bill?  (Read 3920 times)
Metal Halide Boy
Does low power factor affect electric bill? « on: May 15, 2024, 10:09:45 PM » Author: Metal Halide Boy
I have been running a 175 watt MV Westinghouse RMA dusk to dawn for a couple years. It has a 120 volt NPF HX ballast. What I was wondering is this. Does the inefficiency of the NPF ballast severely affect the electric bill? Like versus a CWA running on 240 volt or a HPF HX ballast? And also I have wondered, versus a HX, how lossy is a single coil reactor ballast? And yes of course a reactor would be running at 240 volts, and I have been led to beleive that operation at 240v makes any light cheaper to run.
HIDLad001
GoL UCwvPaxz1-rbLAjLpk55zl1A
Re: Does low power factor affect electric bill? « Reply #1 on: May 16, 2024, 08:29:22 AM » Author: HIDLad001
Not usually. If you are a normal customer, they are billing you for real power in kWh which accounts for power factor in the equation of voltage times current to get the *real power*.
But if you are an industrial customer, you can be being billed for apparent power in kVArh (which doesn’t account for power factor and just straight up multiplies the voltage by the current), then you will be charged more for a low power factor.
But chances are you’re not because apparent power is only Really charged to industrial customers, and not residential customers.
Re: Does low power factor affect electric bill? « Reply #2 on: May 16, 2024, 08:35:55 AM » Author: Mandolin Girl
It won't make any difference to your bill, but it will make a difference to the power used. The lamp will draw more current and if you're on the brink of the maximum capacity of the wiring, it could push you over.
Personally I always like to make sure the PF of my discharge lamp circuits is as high as possible. Here, that's usually done with a capacitor across the supply, it's often different on your side of the water.
Re: Does low power factor affect electric bill? « Reply #3 on: May 16, 2024, 08:52:41 AM » Author: Mandolin Girl
We noticed a big difference to how our Goldeye ran after installing the correct rating of capacitor to bring the PF up to .85 from .4 (ish)  :wndr:
Before it was running really hot and needed additional cooling, but not after the work had been done.  8)
Metal Halide Boy
Re: Does low power factor affect electric bill? « Reply #4 on: May 16, 2024, 08:56:13 AM » Author: Metal Halide Boy
That's what I thought, but I wasn't sure. Thanks!
Laurens
Re: Does low power factor affect electric bill? « Reply #5 on: May 16, 2024, 12:13:48 PM » Author: Laurens
Your low power factor is not directly metered. However, if "everyone" has a low power factor, the transmission cost of the electricity will go up. Because, as Rommie said, although the low power factor is not registered as power used, it does impact the current running through the conductors in the grid, in the transformers and in your home. Eventually that gets factored into everyone's power bill, so it's always best to compensate loads with a bad power factor.
We used to have a tanning bed with 10x 100w fluorescents, with conventional 230v choke ballasts, and no compensation capacitors. Although 1000w (4,3 ampere) is easily handled (at our 230v mains here) by any bog standard appliance cable, the cable on the tanning bed got seriously warm and soft. This was because the power factor of the choke ballast and lamp is together 0,53. that makes it look as if there was 8 ampere flowing through the cable.
It likely was a 3x 0,75mm2 cable, which would be fine for 1000w appliances, but woefully insufficient for 8 ampere, or loads that 'look like 2000w'.  But i do not remember what cable was on it, sadly. 2000w heaters often run on 1,5mm2 cords and not heat up, so they likely seriously miscalculated the load on the cord.
The appropriate capacitor for the 100w ballasts here is 8µF, and an 80µF mains rated capacitor would've added significantly to the cost, so likely left out for that reason.
There should be no effect on how hot a ballast gets, it does not influence the current running through the ballast if it's just a compensation capacitor parallel to the mains connection.
Re: Does low power factor affect electric bill? « Reply #6 on: May 16, 2024, 12:19:07 PM » Author: Rommie
It shouldn't have affected how hot the ballast got, but I can assure you it did. We needed a fan pointing at the fixture before adding PFC, but not afterwards. I don't recall the exact temperature figures, but it was significant.
Laurens
Re: Does low power factor affect electric bill? « Reply #7 on: May 16, 2024, 12:46:30 PM » Author: Laurens
Huh, that's very interesting and odd. I'll try and see what happens, when i remove the capacitor from my 80w MV ballast.
