It might be bad fixture sealing - humidity on the surface lower electrical field around electrodes, so it require higher starting voltage. Solution is to repair the sealing and/or replace luminaires. Lamp's age might be a factor too, as they are older, it is harder to start them and when the humidity add, it does not light anymore. If this happen after few years, lamps rated life is spent, so no wonder. To avoid problems, good practice is to schedule replacement at ~75..80% of rated life, assume good quality lamps (rated life is or the light output is more then 30% below initial, or when 50% of lamps die, so mainly the secont criterium require sooner replacement to not have half fixtures dead).
|
|
|