Osha report on someone dying of electrocution replacing fluorescent tubes « on: March 31, 2021, 05:01:08 AM » Author: HomeBrewLamps
https://www.osha.gov/pls/imis/accidentsearch.accident_detail?id=201127594

Could a ballast failure really cause 700 volts?
Logged

~Owen

:colorbulb: Scavenger, Urban Explorer, Lighting Enthusiast and Creator of homebrewlamps 8) :colorbulb:

joseph_125
Member
*****
Offline

Gender: Male
View Posts
View Gallery


GoL
Re: Osha report on someone dying of electrocution replacing fluorescent tubes « Reply #1 on: March 31, 2021, 05:16:47 AM » Author: joseph_125
Sign ballast? Some of those have rather high open circuit voltages and voltage to grounds. Especially the larger multi lamp units as they ran the lamps all in series.
Logged
Medved
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Re: Osha report on someone dying of electrocution replacing fluorescent tubes « Reply #2 on: March 31, 2021, 06:45:59 AM » Author: Medved
https://www.osha.gov/pls/imis/accidentsearch.accident_detail?id=201127594

Could a ballast failure really cause 700 volts?

The thing is, you need such voltage for the lamp ignition, there is no way around that.

Mainly with old US IS magnetic ballast it is not only in failure mode, but also during normal operation when there is lamp missing. It is just the ballast OCV.

There should be a cutout contact/switch at the cold end tube socket (to disconnect the ballast when there is no tube inserted), but when the lamp is inserted, the voltage is there. So if there was some dirt on the tube causing leakage from the hot contact to the tube surface or the tube or sockets are damaged and so the live wiring gets exposed, you may easily get shocked by this.

The modern electronic ballasts deliver the ignition for just in short time (a second or so), either once after power ON or repeating with few second gap, so when touched limit the exposure and give breaks to allow muscles to release the grip, greatly reducing the risk of health consequences. Plus the voltage is of high frequency, which is of less risk for severe shock injury, it becomes more of a burn than electrocution risk.
There indeed the failure of the ignition sequecer may cause the high voltage to be present for longer time than designed so become dangerous. But usually the ballast circuit is stressed by that state quite a lot, so it physically would not survive that state for too long.

So to me it was not the ballast failure, but either the tube or socket failure, together with inadequate work practices (touching the dangerous areas without checking their safety, PPE,...) then led to the deadly accident...
Logged

No more selfballasted c***

HomeBrewLamps
Member
*****
Offline

Gender: Male
View Posts
View Gallery


SodiumVapor 105843202020668111118 UCpGClK_9OH8N4QkD1fp-jNw majorpayne1226 187567902@N04/
Re: Osha report on someone dying of electrocution replacing fluorescent tubes « Reply #3 on: April 02, 2021, 03:40:05 AM » Author: HomeBrewLamps
Interesting analysis. I completely forgot about the sockets with disconnect switches in them!
Logged

~Owen